• Calculate runtime for backup battery

    From AK@21:1/5 to All on Thu Sep 8 02:57:35 2022
    This is what I am using for backup for my computer.

    Expert Power EXP 12180 12 volts 18 amp hours

    My Xfinity modem uses 22 watts.
    LG monitor 60 watts
    Computer 55 watts
    Grand total of power usage is 137 watts.

    Is there a calculation that will show how many hours my computer will run using the backup battery?

    Thanks.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From R.Wieser@21:1/5 to All on Thu Sep 8 13:53:16 2022
    AK,

    Is there a calculation that will show how many hours my computer will run using the backup battery?

    Yes.

    A "Watt" is roughly equivalent to a "Volt times Ampere". This means your backup battery contains 12 volt times 18 Amp hours equals 216 watt hours.

    By dividing that by the 137 Watt you draw from it you get how many hours it will last : 216 watt hours divided by 137 watts equals 1.57 hours (one hour,
    34 minutes).


    Mind you, the above is just a crude calculation, which does not account for
    how many amperes you draw from it, the age of the battery (a charge declines due to age), how many times and how fast it was charged or even temperature. And all of that is ofcourse dependant on the type of battery (lead-acid batteries respond differentlly that lithium-ion ones).

    Hope that helps.
    Rudy Wieser

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Paul@21:1/5 to All on Thu Sep 8 10:06:56 2022
    On 9/8/2022 5:57 AM, AK wrote:
    This is what I am using for backup for my computer.

    Expert Power EXP 12180 12 volts 18 amp hours

    My Xfinity modem uses 22 watts.
    LG monitor 60 watts
    Computer 55 watts
    Grand total of power usage is 137 watts.

    Is there a calculation that will show how many hours my computer will run using the backup battery?

    Thanks.


    UPS manufacturers have a prediction curve, which de-rates
    battery capacity, for the rate of discharge. Visiting the
    web site for the UPS product, can sometimes cough up that
    graph.

    The capacity is not a "conserved" quantity.

    It goes like this.

    Load You predict You get

    100W 8 minutes 8 minutes
    200W 4 minutes 3 minutes
    400W 2 minutes 1.2 minutes

    As you honk on the battery, more of the energy is lost
    as heat inside the battery. You're talking 40 amp flows
    from the battery. Notice that the UPS has bloody fat wires
    on top to the battery. That means there's a serious DC current
    flow at full UPS load. Those wires are kept short, because
    among other things, that wire costs money. That wire, at
    least the wire on mine, is the "very nice" kind. Not
    RadioShack wire :-) (RadioShack refused to sell nickel
    plated wire, so I hated them for that...)

    *******

    https://www.apcguard.com/Smart-UPS-Runtime-Chart.asp

    Let's just take the top entry, and Half versus Full load.

    Half 24 minutes 240W
    Full 7 minutes 480W

    You can see the battery doesn't like this. You can go down the
    chart and take ratios of half versus full, and see whether the
    behavior is a "manifest constant", or whether each unit is
    different.

    What you'd really want, is check for manifest constant behavior,
    for units that use the *same* battery. You would hope in such
    a case, the same ratio presents itself, at the same load values.

    In any case, that page gives you at least something to plot up
    and consider for your maths.

    *******

    UPS are rated in terms of Watts and VA. The difference between
    these two units of measure, is the PF or power factor. This
    is a measure of whether the voltage and current waveforms are
    out of phase. Modern ATX supplies have Active Power Factor Correction
    or PFC, which attempts to make the load PF=1 or resistive, the
    best kind of resistive. The power company prefers we use
    resistive loads, like an incandescent bulb is PF=1.

    If you take all the electrical loads, put them on a power strip,
    then plug the power strip into one of these, you can measure
    W, VA, and PF, with the one instrument. One of these should
    be about $40 or so. I have one monitoring my "pig" computer,
    as a reminder of what a pig it is. It costs real money to run
    the pig.

    http://www.p3international.com/products/p4400.html

    There is also a version of this, for other markets
    with different plug. The design limit of 15 amps is
    a function of the shunt inside, and the shunt won't
    change between markets. But one meter expects 120V,
    the other model expects 240V max. There's probably
    a different scaling resistor used for volts. And a different
    firmware for the processor in there (maths are done
    in real time).

    I don't know if any UPS website has worked examples of
    W and VA, and what to do with the numbers. But it would
    certainly help if they did.

    Paul

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From AK@21:1/5 to R.Wieser on Thu Sep 8 12:04:26 2022
    On Thursday, September 8, 2022 at 6:53:57 AM UTC-5, R.Wieser wrote:
    AK,
    Is there a calculation that will show how many hours my computer will run using the backup battery?
    Yes.

    A "Watt" is roughly equivalent to a "Volt times Ampere". This means your backup battery contains 12 volt times 18 Amp hours equals 216 watt hours.

    By dividing that by the 137 Watt you draw from it you get how many hours it will last : 216 watt hours divided by 137 watts equals 1.57 hours (one hour, 34 minutes).


    Mind you, the above is just a crude calculation, which does not account for how many amperes you draw from it, the age of the battery (a charge declines due to age), how many times and how fast it was charged or even temperature. And all of that is ofcourse dependant on the type of battery (lead-acid batteries respond differentlly that lithium-ion ones).

    Hope that helps.
    Rudy Wieser
    Thanks Rudy.

    My 137 watts came from using a Watt O Meter, so it should be fairly accurate.

    It is a sealed lead acid battery.

    Andy

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From AK@21:1/5 to R.Wieser on Thu Sep 8 14:03:43 2022
    On Thursday, September 8, 2022 at 3:30:18 PM UTC-5, R.Wieser wrote:
    AK,

    Thanks Rudy.

    You're welcome.
    My 137 watts came from using a Watt O Meter, so it should be fairly accurate.
    Even better (your message read as if you had taken the wattage values off of the labels of each device and added them together).

    Mind though that when I said "roughly equivalent" I didn't account for any kind of phase-shifting between the voltage and current cycles. When you
    would be measuring the voltage and current independantly with the apropriate equipment you might well find a higher current than what the drawn wattage seems to indicate (but gets obsfucated by the phase-shifting).

    IOW, the time I've calculated is an *optimum* time, the real one could be well lower - also because of the number of other factors I named.
    It is a sealed lead acid battery.
    I'm sorry, but I've not been enough "in to it" to know how much difference
    it makes on the current you're drawing from it. Just don't take the calculated time as show long it will actually last. Drawing ~11.5 amps (137 watts divided by 12 volts) is not a small ammount.

    Also, the voltage conversion (from the batteries 12 to the output 220 volts) also causes some loss.

    Did I already say it was a crude calculation ? :-)

    Regards,
    Rudy Wieser
    My old Frontier modem did not draw much current and did not heat up much.

    But then I got only 15 Mbps download speed.

    With my Xfinity modem, I get 320 Mbps speed.

    But it generates a lot of heat. :-(

    My power outages tend to last no more than a few minutes.

    Andy

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From R.Wieser@21:1/5 to All on Thu Sep 8 22:29:43 2022
    AK,

    Thanks Rudy.

    You're welcome.

    My 137 watts came from using a Watt O Meter, so it should be fairly
    accurate.

    Even better (your message read as if you had taken the wattage values off of the labels of each device and added them together).

    Mind though that when I said "roughly equivalent" I didn't account for any
    kind of phase-shifting between the voltage and current cycles. When you would be measuring the voltage and current independantly with the apropriate equipment you might well find a higher current than what the drawn wattage seems to indicate (but gets obsfucated by the phase-shifting).

    IOW, the time I've calculated is an *optimum* time, the real one could be
    well lower - also because of the number of other factors I named.

    It is a sealed lead acid battery.

    I'm sorry, but I've not been enough "in to it" to know how much difference
    it makes on the current you're drawing from it. Just don't take the calculated time as show long it will actually last. Drawing ~11.5 amps (137 watts divided by 12 volts) is not a small ammount.

    Also, the voltage conversion (from the batteries 12 to the output 220 volts) also causes some loss.

    Did I already say it was a crude calculation ? :-)

    Regards,
    Rudy Wieser

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Paul@21:1/5 to All on Thu Sep 8 22:27:48 2022
    On 9/8/2022 5:03 PM, AK wrote:
    On Thursday, September 8, 2022 at 3:30:18 PM UTC-5, R.Wieser wrote:
    AK,

    Thanks Rudy.

    You're welcome.
    My 137 watts came from using a Watt O Meter, so it should be fairly
    accurate.
    Even better (your message read as if you had taken the wattage values off of >> the labels of each device and added them together).

    Mind though that when I said "roughly equivalent" I didn't account for any >> kind of phase-shifting between the voltage and current cycles. When you
    would be measuring the voltage and current independantly with the apropriate >> equipment you might well find a higher current than what the drawn wattage >> seems to indicate (but gets obsfucated by the phase-shifting).

    IOW, the time I've calculated is an *optimum* time, the real one could be
    well lower - also because of the number of other factors I named.
    It is a sealed lead acid battery.
    I'm sorry, but I've not been enough "in to it" to know how much difference >> it makes on the current you're drawing from it. Just don't take the
    calculated time as show long it will actually last. Drawing ~11.5 amps (137 >> watts divided by 12 volts) is not a small ammount.

    Also, the voltage conversion (from the batteries 12 to the output 220 volts) >> also causes some loss.

    Did I already say it was a crude calculation ? :-)

    Regards,
    Rudy Wieser
    My old Frontier modem did not draw much current and did not heat up much.

    But then I got only 15 Mbps download speed.

    With my Xfinity modem, I get 320 Mbps speed.

    But it generates a lot of heat. :-(

    My power outages tend to last no more than a few minutes.

    Andy


    With lead acid batteries, even the sealed ones, the idea is
    the battery provides time to do a controlled shutdown of the
    PC. Then, you flip off the power on the lot.

    This reduces the "depth of discharge", and is intended to
    make the battery last longer (in years). I got 11 years
    from the first battery, only 4 years from the second battery.
    The replacement batteries are not very good. The failure
    mode of the second battery was different -- it seemed
    to be plate failure, destruction of plates. Three of six
    cells failed short.

    Paul

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From AK@21:1/5 to Paul on Fri Sep 9 05:03:39 2022
    On Thursday, September 8, 2022 at 9:27:53 PM UTC-5, Paul wrote:
    On 9/8/2022 5:03 PM, AK wrote:
    On Thursday, September 8, 2022 at 3:30:18 PM UTC-5, R.Wieser wrote:
    AK,

    Thanks Rudy.

    You're welcome.
    My 137 watts came from using a Watt O Meter, so it should be fairly
    accurate.
    Even better (your message read as if you had taken the wattage values off of
    the labels of each device and added them together).

    Mind though that when I said "roughly equivalent" I didn't account for any >> kind of phase-shifting between the voltage and current cycles. When you
    would be measuring the voltage and current independantly with the apropriate
    equipment you might well find a higher current than what the drawn wattage >> seems to indicate (but gets obsfucated by the phase-shifting).

    IOW, the time I've calculated is an *optimum* time, the real one could be >> well lower - also because of the number of other factors I named.
    It is a sealed lead acid battery.
    I'm sorry, but I've not been enough "in to it" to know how much difference >> it makes on the current you're drawing from it. Just don't take the
    calculated time as show long it will actually last. Drawing ~11.5 amps (137
    watts divided by 12 volts) is not a small ammount.

    Also, the voltage conversion (from the batteries 12 to the output 220 volts)
    also causes some loss.

    Did I already say it was a crude calculation ? :-)

    Regards,
    Rudy Wieser
    My old Frontier modem did not draw much current and did not heat up much.

    But then I got only 15 Mbps download speed.

    With my Xfinity modem, I get 320 Mbps speed.

    But it generates a lot of heat. :-(

    My power outages tend to last no more than a few minutes.

    Andy

    With lead acid batteries, even the sealed ones, the idea is
    the battery provides time to do a controlled shutdown of the
    PC. Then, you flip off the power on the lot.

    This reduces the "depth of discharge", and is intended to
    make the battery last longer (in years). I got 11 years
    from the first battery, only 4 years from the second battery.
    The replacement batteries are not very good. The failure
    mode of the second battery was different -- it seemed
    to be plate failure, destruction of plates. Three of six
    cells failed short.

    Paul
    My current battery is 4 yrs old.

    Andy

    --- SoupGate-Win32 v1.05