    Have a fluorescent fitting which I retrofitted an LED tube to. All worked
    fine.

    Upgraded to a smart switch. The wiring in the box is just 2 wires - live
    and load. All worked fine with live to "L" and load to "L1".

    Smart switch failed after 6 months - the little LED comes on and goes off
    when you press and hold the switch, but nada.

    Sourced a replacement while waiting for the exchange. Slightly different
    look but same connections. However this didn't work.

    I wired it into a L+N test rig and it works fine.

    Back to the light - I connected a capacitor that was supplied with a
    different smart switch across the incoming live and neutral in the light fitting. Still no joy.

    The switch instructions show a non-neutral setup with a capacitor across
    the load. So this isn't unsupported. Moreover I had a switch which *did*
    work.

    Clearly I am missing a trick here. Does this make sense to anyone else ?

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From David Wade@21:1/5 to All on Tue Dec 24 12:52:38 2024
    On 24/12/2024 11:34, Jethro_uk wrote:
    Have a fluorescent fitting which I retrofitted an LED tube to. All worked fine.

    Upgraded to a smart switch. The wiring in the box is just 2 wires - live
    and load. All worked fine with live to "L" and load to "L1".

    Smart switch failed after 6 months - the little LED comes on and goes off when you press and hold the switch, but nada.

    Sourced a replacement while waiting for the exchange. Slightly different
    look but same connections. However this didn't work.

    I wired it into a L+N test rig and it works fine.

    Back to the light - I connected a capacitor that was supplied with a different smart switch across the incoming live and neutral in the light fitting. Still no joy.

    The switch instructions show a non-neutral setup with a capacitor across
    the load. So this isn't unsupported. Moreover I had a switch which *did* work.

    Clearly I am missing a trick here. Does this make sense to anyone else ?

    Is the the sort of switch where you push it and the light switches on
    for a set period of time?

    I tried several versions for my downstairs loo with and without a
    capacitor, but none lasted more than a few months...

    .. in desperation I tried an old fashioned pneumatic plunger but that
    didn't stay on long enough for me to finish the crossword, so in the end
    I wired the switch permanently on and fitted an infra-red sensor from
    screwfix.

    It can be set accurately and a quick wave will re-start the time should
    I be struggling with the crossword. Its been there for nearly two years
    now and still works fine...

    Dave

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jethro_uk@21:1/5 to Theo on Tue Dec 24 11:45:06 2024
    On Tue, 24 Dec 2024 11:22:35 +0000, Theo wrote:

    Jethro_uk <jethro_uk@hotmailbin.com> wrote:
    Have a fluorescent fitting which I retrofitted an LED tube to. All
    worked fine.

    Upgraded to a smart switch. The wiring in the box is just 2 wires -
    live and load. All worked fine with live to "L" and load to "L1".

    Smart switch failed after 6 months - the little LED comes on and goes
    off when you press and hold the switch, but nada.

    Sourced a replacement while waiting for the exchange. Slightly
    different look but same connections. However this didn't work.

    I wired it into a L+N test rig and it works fine.

    Back to the light - I connected a capacitor that was supplied with a
    different smart switch across the incoming live and neutral in the
    light fitting. Still no joy.

    The switch instructions show a non-neutral setup with a capacitor
    across the load. So this isn't unsupported. Moreover I had a switch
    which *did* work.

    Clearly I am missing a trick here. Does this make sense to anyone else
    ?

    Some no-neutral smart switches acquire power by trickling current
    through the load, which gives them enough voltage drop to scavenge
    power. That only works with a filament bulb because you can't trickle through a fluoro or some forms of LED PSU. Have you changed the LED recently?

    Otherwise I think they try to harvest power when the light is on, when there's enough current flowing to cause a voltage drop, and store that
    in a supercap. That only works if the light is on regularly enough to
    charge the supercap.

    I suppose putting a cap in series with the load might act as a
    capacitive dropper and also offer some voltage drop.

    The one variable here is the LED driver, which is something the switch doesn't know anything about. All this trickling and dropping only works
    if the load will allow current to flow. Maybe your switch and tube combination are incompatible? Maybe there's something about fluoro-replacements that make them look different from bulbs?

    Unfortunately no-neutral switches are a hack at best, so it might be
    trial and error to find something that works. A filament should, but I
    don't know about fluoros or fluoro-replacements.

    Or get one with a battery that doesn't need to scavenge power?

    Thanks for that. It's a little frustrating as until it decided to not
    work, the one I had in place worked fine for 6 months. Hopefully I will
    get an identical one from the vendor in the new year.

    I'm not too bent out of shape as the one I'm trying now was less than £8
    from China in 6 days.

    I agree the LED drop-in replacement for the fluorescent tube is the
    unknown quantity here. All my other smart switches work fine with no
    neutral and "regular" LED lamps.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Theo@21:1/5 to jethro_uk@hotmailbin.com on Tue Dec 24 11:22:35 2024
    Jethro_uk <jethro_uk@hotmailbin.com> wrote:
    Have a fluorescent fitting which I retrofitted an LED tube to. All worked fine.

    Upgraded to a smart switch. The wiring in the box is just 2 wires - live
    and load. All worked fine with live to "L" and load to "L1".

    Smart switch failed after 6 months - the little LED comes on and goes off when you press and hold the switch, but nada.

    Sourced a replacement while waiting for the exchange. Slightly different
    look but same connections. However this didn't work.

    I wired it into a L+N test rig and it works fine.

    Back to the light - I connected a capacitor that was supplied with a different smart switch across the incoming live and neutral in the light fitting. Still no joy.

    The switch instructions show a non-neutral setup with a capacitor across
    the load. So this isn't unsupported. Moreover I had a switch which *did* work.

    Clearly I am missing a trick here. Does this make sense to anyone else ?

    Some no-neutral smart switches acquire power by trickling current through
    the load, which gives them enough voltage drop to scavenge power. That only works with a filament bulb because you can't trickle through a fluoro or
    some forms of LED PSU. Have you changed the LED recently?

    Otherwise I think they try to harvest power when the light is on, when
    there's enough current flowing to cause a voltage drop, and store that in a supercap. That only works if the light is on regularly enough to charge the supercap.

    I suppose putting a cap in series with the load might act as a capacitive dropper and also offer some voltage drop.

    The one variable here is the LED driver, which is something the switch
    doesn't know anything about. All this trickling and dropping only works if
    the load will allow current to flow. Maybe your switch and tube combination are incompatible? Maybe there's something about fluoro-replacements that
    make them look different from bulbs?

    Unfortunately no-neutral switches are a hack at best, so it might be trial
    and error to find something that works. A filament should, but I don't know about fluoros or fluoro-replacements.

    Or get one with a battery that doesn't need to scavenge power?

    Theo

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Tricky Dicky@21:1/5 to David Wade on Tue Dec 24 12:40:53 2024
    David Wade <dave@g4ugm.invalid> wrote:
    On 24/12/2024 11:34, Jethro_uk wrote:
    Have a fluorescent fitting which I retrofitted an LED tube to. All worked
    fine.

    Upgraded to a smart switch. The wiring in the box is just 2 wires - live
    and load. All worked fine with live to "L" and load to "L1".

    Smart switch failed after 6 months - the little LED comes on and goes off
    when you press and hold the switch, but nada.

    Sourced a replacement while waiting for the exchange. Slightly different
    look but same connections. However this didn't work.

    I wired it into a L+N test rig and it works fine.

    Back to the light - I connected a capacitor that was supplied with a
    different smart switch across the incoming live and neutral in the light
    fitting. Still no joy.

    The switch instructions show a non-neutral setup with a capacitor across
    the load. So this isn't unsupported. Moreover I had a switch which *did*
    work.

    Clearly I am missing a trick here. Does this make sense to anyone else ?

    Is the the sort of switch where you push it and the light switches on
    for a set period of time?

    I tried several versions for my downstairs loo with and without a
    capacitor, but none lasted more than a few months...

    .. in desperation I tried an old fashioned pneumatic plunger but that
    didn't stay on long enough for me to finish the crossword, so in the end
    I wired the switch permanently on and fitted an infra-red sensor from screwfix.

    It can be set accurately and a quick wave will re-start the time should
    I be struggling with the crossword. Its been there for nearly two years
    now and still works fine...

    Dave


    When I re-wired our bungalow I did consider looping in at the switches thus providing a neutral but owing to the fact that the roof pitch is so shallow
    you cannot stand up in our loft and possibly working in the extremes of
    the trusses, I opted for running a series of Wago boxes down the spine of
    the house branching off to the switches and rosettes. The plan being to use Quinetic switches where I want smart functionality by simply removing the switch wire and wiring in a Quinetic WiFi receiver at each Wago box where I need smart functionality and replacing the switch plate with a Quinetic
    switch this would enable switching either with the switch or Alexa voice control.

    Richard

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jethro_uk@21:1/5 to All on Fri Dec 27 15:09:16 2024
    On Tue, 24 Dec 2024 11:45:06 +0000, Jethro_uk wrote:

    On Tue, 24 Dec 2024 11:22:35 +0000, Theo wrote:

    Jethro_uk <jethro_uk@hotmailbin.com> wrote:
    Have a fluorescent fitting which I retrofitted an LED tube to. All
    worked fine.

    Upgraded to a smart switch. The wiring in the box is just 2 wires -
    live and load. All worked fine with live to "L" and load to "L1".

    Smart switch failed after 6 months - the little LED comes on and goes
    off when you press and hold the switch, but nada.

    Sourced a replacement while waiting for the exchange. Slightly
    different look but same connections. However this didn't work.

    I wired it into a L+N test rig and it works fine.

    Back to the light - I connected a capacitor that was supplied with a
    different smart switch across the incoming live and neutral in the
    light fitting. Still no joy.

    The switch instructions show a non-neutral setup with a capacitor
    across the load. So this isn't unsupported. Moreover I had a switch
    which *did* work.

    Clearly I am missing a trick here. Does this make sense to anyone else
    ?

    Some no-neutral smart switches acquire power by trickling current
    through the load, which gives them enough voltage drop to scavenge
    power. That only works with a filament bulb because you can't trickle
    through a fluoro or some forms of LED PSU. Have you changed the LED
    recently?

    Otherwise I think they try to harvest power when the light is on, when
    there's enough current flowing to cause a voltage drop, and store that
    in a supercap. That only works if the light is on regularly enough to
    charge the supercap.

    I suppose putting a cap in series with the load might act as a
    capacitive dropper and also offer some voltage drop.

    The one variable here is the LED driver, which is something the switch
    doesn't know anything about. All this trickling and dropping only
    works if the load will allow current to flow. Maybe your switch and
    tube combination are incompatible? Maybe there's something about
    fluoro-replacements that make them look different from bulbs?

    Unfortunately no-neutral switches are a hack at best, so it might be
    trial and error to find something that works. A filament should, but I
    don't know about fluoros or fluoro-replacements.

    Or get one with a battery that doesn't need to scavenge power?

    Thanks for that. It's a little frustrating as until it decided to not
    work, the one I had in place worked fine for 6 months. Hopefully I will
    get an identical one from the vendor in the new year.

    I'm not too bent out of shape as the one I'm trying now was less than £8 from China in 6 days.

    I agree the LED drop-in replacement for the fluorescent tube is the
    unknown quantity here. All my other smart switches work fine with no
    neutral and "regular" LED lamps.

    As an update to this:

    while waiting for (hopefully) a like for like replacement from the
    original (works with my LED replacement for fluoro tube), I thought I
    would try the new switch in a different fitting - with 3xLED bayonet type
    lamps and no neutral.

    Still didn't work.

    Annoyingly all my switched lights are LED or LED replacements for fluoros,
    so options are limited.

    Unusually, I must have got lucky with the original design of smart switch
    for it to work with 4 LED lamps of various stripes.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Jethro_uk@21:1/5 to All on Mon Dec 30 12:27:05 2024
    Replacement switch arrived today.

    Idiot courier tried to jam it through the letterbox which managed to
    shatter the glass cover. Luckily I had the old one so it was an
    irritation rather than an issue.

    Connected it in and it worked perfectly.

    Clearly not all "no neutral" devices are equal.