• Re: 2-port and 3-port CH valves

    From Mr Paul Briley@21:1/5 to All on Fri Jan 17 21:15:04 2025
    Can I put and 2 port value and a 3 port value in same system

    --
    For full context, visit https://www.homeownershub.com/uk-diy/2-port-and-3-port-ch-valves-450655-.htm

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Peter Able@21:1/5 to Mr Paul Briley on Sat Jan 18 09:54:14 2025
    On 17/01/2025 21:15, Mr Paul Briley wrote:
    Can I put and 2 port value and a 3 port value in same system



    Yes - but why? My fully-pumped system has just a single two-port valve.

    --
    PA
    --

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From alan_m@21:1/5 to Peter Able on Sat Jan 18 11:37:11 2025
    On 18/01/2025 09:54, Peter Able wrote:
    On 17/01/2025 21:15, Mr Paul Briley wrote:
    Can I put and 2 port value and a 3 port value in same system



    Yes - but why?  My fully-pumped system has just a single two-port valve.


    Perhaps a 3 port for DHW and zone 1 and then additional 2 ports for
    zones 2,3,...n?

    I cannot see a problem as long as the system is designed properly and a controlled has the necessary means of control.

    --
    mailto : news {at} admac {dot} myzen {dot} co {dot} uk

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From John Rumm@21:1/5 to All on Sat Jan 18 14:48:49 2025
    On 18/01/2025 11:37, alan_m wrote:
    On 18/01/2025 09:54, Peter Able wrote:
    On 17/01/2025 21:15, Mr Paul Briley wrote:
    Can I put and 2 port value and a 3 port value in same system



    Yes - but why?  My fully-pumped system has just a single two-port valve.


    Perhaps a 3 port for DHW and zone 1 and then additional 2 ports for
    zones 2,3,...n?

    I cannot see a problem as long as the system is designed properly and a controlled has the necessary means of control.

    Indeed. All the required info for wiring etc, can be found here:

    https://wiki.diyfaq.org.uk/index.php/Central_Heating_Controls_and_Zoning


    --
    Cheers,

    John.

    /=================================================================\
    | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------|
    | John Rumm - john(at)internode(dot)co(dot)uk | \=================================================================/

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Peter Able@21:1/5 to All on Sun Jan 19 09:23:17 2025
    On 18/01/2025 11:37, alan_m wrote:
    On 18/01/2025 09:54, Peter Able wrote:
    On 17/01/2025 21:15, Mr Paul Briley wrote:
    Can I put and 2 port value and a 3 port value in same system



    Yes - but why?  My fully-pumped system has just a single two-port valve.


    Perhaps a 3 port for DHW and zone 1 and then additional 2 ports for
    zones 2,3,...n?

    I cannot see a problem as long as the system is designed properly and a controlled has the necessary means of control.


    Have you shares in Honeywell? ;-}
    PA
    --

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From fred@21:1/5 to Peter Able on Sun Jan 19 10:01:22 2025
    Peter Able <stuck@home.com> wrote in news:vmiga6$23k1r$1@dont-email.me:

    On 18/01/2025 11:37, alan_m wrote:
    On 18/01/2025 09:54, Peter Able wrote:
    On 17/01/2025 21:15, Mr Paul Briley wrote:
    Can I put and 2 port value and a 3 port value in same system



    Yes - but why?  My fully-pumped system has just a single two-port
    valve.


    Perhaps a 3 port for DHW and zone 1 and then additional 2 ports for
    zones 2,3,...n?

    I cannot see a problem as long as the system is designed properly and
    a controlled has the necessary means of control.


    Have you shares in Honeywell? ;-}


    Not actually as much of a joke as you think. Default setting for Honeywell stats is to cycle them multiple times an hour for closer temperature
    control. Do that and your expensive motorised control valves will need
    changed every couple of years.

    Voice of experience from one with a one zone per room heating system using motorised valves, soon to be switched to thermal actuators. Honeywell stats changed to simple on-off control ones in the interim.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From SteveW@21:1/5 to fred on Sun Jan 19 17:32:19 2025
    On 19/01/2025 10:01, fred wrote:
    Peter Able <stuck@home.com> wrote in news:vmiga6$23k1r$1@dont-email.me:

    On 18/01/2025 11:37, alan_m wrote:
    On 18/01/2025 09:54, Peter Able wrote:
    On 17/01/2025 21:15, Mr Paul Briley wrote:
    Can I put and 2 port value and a 3 port value in same system



    Yes - but why?  My fully-pumped system has just a single two-port
    valve.


    Perhaps a 3 port for DHW and zone 1 and then additional 2 ports for
    zones 2,3,...n?

    I cannot see a problem as long as the system is designed properly and
    a controlled has the necessary means of control.


    Have you shares in Honeywell? ;-}


    Not actually as much of a joke as you think. Default setting for Honeywell stats is to cycle them multiple times an hour for closer temperature
    control. Do that and your expensive motorised control valves will need changed every couple of years.

    Voice of experience from one with a one zone per room heating system using motorised valves, soon to be switched to thermal actuators. Honeywell stats changed to simple on-off control ones in the interim.

    I too have one zone per room heating (not Honeywell stats) and in the 21
    years that I have had it, the most frequently switched (hot water
    cylinder) has failed (motor only) a number of times and the least used
    (kitchen kick-space heater) similarly. The rest just continue to run and
    run.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Peter Able@21:1/5 to SteveW on Sun Jan 19 19:39:47 2025
    On 19/01/2025 17:32, SteveW wrote:
    On 19/01/2025 10:01, fred wrote:
    Peter Able <stuck@home.com> wrote in news:vmiga6$23k1r$1@dont-email.me:

    On 18/01/2025 11:37, alan_m wrote:
    On 18/01/2025 09:54, Peter Able wrote:
    On 17/01/2025 21:15, Mr Paul Briley wrote:
    Can I put and 2 port value and a 3 port value in same system



    Yes - but why?  My fully-pumped system has just a single two-port
    valve.


    Perhaps a 3 port for DHW and zone 1 and then additional 2 ports for
    zones 2,3,...n?

    I cannot see a problem as long as the system is designed properly and
    a controlled has the necessary means of control.


    Have you shares in Honeywell? ;-}


    Not actually as much of a joke as you think. Default setting for
    Honeywell
    stats is to cycle them multiple times an hour for closer temperature
    control. Do that and your expensive motorised control valves will need
    changed every couple of years.

    Voice of experience from one with a one zone per room heating system
    using
    motorised valves, soon to be switched to thermal actuators. Honeywell
    stats
    changed to simple on-off control ones in the interim.

    I too have one zone per room heating (not Honeywell stats) and in the 21 years that I have had it, the most frequently switched (hot water
    cylinder) has failed (motor only) a number of times and the least used (kitchen kick-space heater) similarly. The rest just continue to run and
    run.

    Who was joking! ;<}}

    My single 2-port valve system has been up and running since 2002 - with
    nairy a failure.

    The most reliable component is the one you design out of the system.

    K I S S
    --
    PA
    --

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From SteveW@21:1/5 to Peter Able on Mon Jan 20 00:20:32 2025
    On 19/01/2025 19:39, Peter Able wrote:
    On 19/01/2025 17:32, SteveW wrote:
    On 19/01/2025 10:01, fred wrote:
    Peter Able <stuck@home.com> wrote in news:vmiga6$23k1r$1@dont-email.me:

    On 18/01/2025 11:37, alan_m wrote:
    On 18/01/2025 09:54, Peter Able wrote:
    On 17/01/2025 21:15, Mr Paul Briley wrote:
    Can I put and 2 port value and a 3 port value in same system



    Yes - but why?  My fully-pumped system has just a single two-port >>>>>> valve.


    Perhaps a 3 port for DHW and zone 1 and then additional 2 ports for
    zones 2,3,...n?

    I cannot see a problem as long as the system is designed properly and >>>>> a controlled has the necessary means of control.


    Have you shares in Honeywell? ;-}


    Not actually as much of a joke as you think. Default setting for
    Honeywell
    stats is to cycle them multiple times an hour for closer temperature
    control. Do that and your expensive motorised control valves will need
    changed every couple of years.

    Voice of experience from one with a one zone per room heating system
    using
    motorised valves, soon to be switched to thermal actuators. Honeywell
    stats
    changed to simple on-off control ones in the interim.

    I too have one zone per room heating (not Honeywell stats) and in the
    21 years that I have had it, the most frequently switched (hot water
    cylinder) has failed (motor only) a number of times and the least used
    (kitchen kick-space heater) similarly. The rest just continue to run
    and run.

    Who was joking! ;<}}

    My single 2-port valve system has been up and running since 2002 - with
    nairy a failure.

    The most reliable component is the one you design out of the system.

    K I S S

    But you can't set different times and temperatures for each room, to
    only heat them for the times that you are likely to use them. We put our
    system in when our first child was born, to give us the ability to heat
    the living room in the day, his bedroom at night, the kitchen in the
    evening, the hall and stairs, plus the bathroom, when we were likely to
    be using them, keep a minimum temperature in our bedroom at night. Later heating the "spare" bedroom, when we had other children and, as the
    children grew older, the conservatory - used as a computer room, so as
    not to have gaming noise in the through living room.

    Our system is more complex, but allows for a great deal of flexibility
    and only heating rooms as and when needed.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Peter Able@21:1/5 to SteveW on Mon Jan 20 10:53:50 2025
    On 20/01/2025 00:20, SteveW wrote:
    On 19/01/2025 19:39, Peter Able wrote:
    On 19/01/2025 17:32, SteveW wrote:
    On 19/01/2025 10:01, fred wrote:
    Peter Able <stuck@home.com> wrote in news:vmiga6$23k1r$1@dont-email.me: >>>>
    On 18/01/2025 11:37, alan_m wrote:
    On 18/01/2025 09:54, Peter Able wrote:
    On 17/01/2025 21:15, Mr Paul Briley wrote:
    Can I put and 2 port value and a 3 port value in same system



    Yes - but why?  My fully-pumped system has just a single two-port >>>>>>> valve.


    Perhaps a 3 port for DHW and zone 1 and then additional 2 ports for >>>>>> zones 2,3,...n?

    I cannot see a problem as long as the system is designed properly and >>>>>> a controlled has the necessary means of control.


    Have you shares in Honeywell? ;-}


    Not actually as much of a joke as you think. Default setting for
    Honeywell
    stats is to cycle them multiple times an hour for closer temperature
    control. Do that and your expensive motorised control valves will need >>>> changed every couple of years.

    Voice of experience from one with a one zone per room heating system
    using
    motorised valves, soon to be switched to thermal actuators.
    Honeywell stats
    changed to simple on-off control ones in the interim.

    I too have one zone per room heating (not Honeywell stats) and in the
    21 years that I have had it, the most frequently switched (hot water
    cylinder) has failed (motor only) a number of times and the least
    used (kitchen kick-space heater) similarly. The rest just continue to
    run and run.

    Who was joking! ;<}}

    My single 2-port valve system has been up and running since 2002 -
    with nairy a failure.

    The most reliable component is the one you design out of the system.

    K I S S

    But you can't set different times and temperatures for each room, to
    only heat them for the times that you are likely to use them. We put our system in when our first child was born, to give us the ability to heat
    the living room in the day, his bedroom at night, the kitchen in the
    evening, the hall and stairs, plus the bathroom, when we were likely to
    be using them, keep a minimum temperature in our bedroom at night. Later heating the "spare" bedroom, when we had other children and, as the
    children grew older, the conservatory - used as a computer room, so as
    not to have gaming noise in the through living room.

    Our system is more complex, but allows for a great deal of flexibility
    and only heating rooms as and when needed.

    Of course it does - at the cost of higher investment and lower reliability.

    I can set each room's target temperature - just not when each is being
    heated. Is that a problem?

    My current annual gas and electricity consumption is, today, 14 MWh and
    4MWh respectively. That's in a 2800sqft detached house on the colder
    side of the UK. Currently just below 2°C out there.
    --
    PA
    --

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From RJH@21:1/5 to SteveW on Mon Jan 20 13:13:11 2025
    On 20 Jan 2025 at 00:20:32 GMT, SteveW wrote:

    On 19/01/2025 19:39, Peter Able wrote:
    On 19/01/2025 17:32, SteveW wrote:
    On 19/01/2025 10:01, fred wrote:
    Peter Able <stuck@home.com> wrote in news:vmiga6$23k1r$1@dont-email.me: >>>>
    On 18/01/2025 11:37, alan_m wrote:
    On 18/01/2025 09:54, Peter Able wrote:
    On 17/01/2025 21:15, Mr Paul Briley wrote:
    Can I put and 2 port value and a 3 port value in same system



    Yes - but why? My fully-pumped system has just a single two-port >>>>>>> valve.


    Perhaps a 3 port for DHW and zone 1 and then additional 2 ports for >>>>>> zones 2,3,...n?

    I cannot see a problem as long as the system is designed properly and >>>>>> a controlled has the necessary means of control.


    Have you shares in Honeywell? ;-}


    Not actually as much of a joke as you think. Default setting for
    Honeywell
    stats is to cycle them multiple times an hour for closer temperature
    control. Do that and your expensive motorised control valves will need >>>> changed every couple of years.

    Voice of experience from one with a one zone per room heating system
    using
    motorised valves, soon to be switched to thermal actuators. Honeywell
    stats
    changed to simple on-off control ones in the interim.

    I too have one zone per room heating (not Honeywell stats) and in the
    21 years that I have had it, the most frequently switched (hot water
    cylinder) has failed (motor only) a number of times and the least used
    (kitchen kick-space heater) similarly. The rest just continue to run
    and run.

    Who was joking! ;<}}> My single 2-port valve system has been up and running >> since 2002 - with
    nairy a failure.

    The most reliable component is the one you design out of the system.

    K I S S

    But you can't set different times and temperatures for each room, to
    only heat them for the times that you are likely to use them. We put our system in when our first child was born, to give us the ability to heat
    the living room in the day, his bedroom at night, the kitchen in the
    evening, the hall and stairs, plus the bathroom, when we were likely to
    be using them, keep a minimum temperature in our bedroom at night. Later heating the "spare" bedroom, when we had other children and, as the
    children grew older, the conservatory - used as a computer room, so as
    not to have gaming noise in the through living room.

    Our system is more complex, but allows for a great deal of flexibility
    and only heating rooms as and when needed.

    It sounds exhausting to me! What happens if the rooms aren't used as planned - someone's out, or watching TV when they'd usually use the computer?

    I did have a Hive system with linked wireless TRVs. I could programme a number of presets - watching TV, having a bath, at the computer, on holiday,
    whatever. It worked after a fashion but I'd often forget to change modes, and in the end I'm not sure I was any more comfortable or wealthy.

    Now (I've moved) I just adjust the TRVs manually, and/or use electric convection heaters. Not sure yet if it's any more economical, but it's certainly more comfortable.

    --
    Cheers, Rob, Sheffield UK

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From SteveW@21:1/5 to RJH on Mon Jan 20 13:48:25 2025
    On 20/01/2025 13:13, RJH wrote:
    On 20 Jan 2025 at 00:20:32 GMT, SteveW wrote:

    On 19/01/2025 19:39, Peter Able wrote:
    On 19/01/2025 17:32, SteveW wrote:
    On 19/01/2025 10:01, fred wrote:
    Peter Able <stuck@home.com> wrote in news:vmiga6$23k1r$1@dont-email.me: >>>>>
    On 18/01/2025 11:37, alan_m wrote:
    On 18/01/2025 09:54, Peter Able wrote:
    On 17/01/2025 21:15, Mr Paul Briley wrote:
    Can I put and 2 port value and a 3 port value in same system >>>>>>>>>


    Yes - but why? My fully-pumped system has just a single two-port >>>>>>>> valve.


    Perhaps a 3 port for DHW and zone 1 and then additional 2 ports for >>>>>>> zones 2,3,...n?

    I cannot see a problem as long as the system is designed properly and >>>>>>> a controlled has the necessary means of control.


    Have you shares in Honeywell? ;-}


    Not actually as much of a joke as you think. Default setting for
    Honeywell
    stats is to cycle them multiple times an hour for closer temperature >>>>> control. Do that and your expensive motorised control valves will need >>>>> changed every couple of years.

    Voice of experience from one with a one zone per room heating system >>>>> using
    motorised valves, soon to be switched to thermal actuators. Honeywell >>>>> stats
    changed to simple on-off control ones in the interim.

    I too have one zone per room heating (not Honeywell stats) and in the
    21 years that I have had it, the most frequently switched (hot water
    cylinder) has failed (motor only) a number of times and the least used >>>> (kitchen kick-space heater) similarly. The rest just continue to run
    and run.

    Who was joking! ;<}}> My single 2-port valve system has been up and running >>> since 2002 - with
    nairy a failure.

    The most reliable component is the one you design out of the system.

    K I S S

    But you can't set different times and temperatures for each room, to
    only heat them for the times that you are likely to use them. We put our
    system in when our first child was born, to give us the ability to heat
    the living room in the day, his bedroom at night, the kitchen in the
    evening, the hall and stairs, plus the bathroom, when we were likely to
    be using them, keep a minimum temperature in our bedroom at night. Later
    heating the "spare" bedroom, when we had other children and, as the
    children grew older, the conservatory - used as a computer room, so as
    not to have gaming noise in the through living room.

    Our system is more complex, but allows for a great deal of flexibility
    and only heating rooms as and when needed.

    It sounds exhausting to me! What happens if the rooms aren't used as planned -
    someone's out, or watching TV when they'd usually use the computer?

    I did have a Hive system with linked wireless TRVs. I could programme a number
    of presets - watching TV, having a bath, at the computer, on holiday, whatever. It worked after a fashion but I'd often forget to change modes, and in the end I'm not sure I was any more comfortable or wealthy.

    Now (I've moved) I just adjust the TRVs manually, and/or use electric convection heaters. Not sure yet if it's any more economical, but it's certainly more comfortable.


    Most rooms tend to be used at the same times on the same day's each week
    (the timer/stats allow different programs to be allocated to each day if required, but we just use a weekday and a weekend program).

    If one is being used when it normally isn't, just hitting the on
    override button on that room's timer/stat will bring it on, either to
    the next off time or for how ever many hours you select. Similarly
    hitting the off override button will turn heating for that room off, if
    you are not going to use it.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From The Natural Philosopher@21:1/5 to SteveW on Mon Jan 20 14:02:44 2025
    On 20/01/2025 13:48, SteveW wrote:
    Most rooms tend to be used at the same times on the same day's each week
    (the timer/stats allow different programs to be allocated to each day if required, but we just use a weekday and a weekend program).

    If one is being used when it normally isn't, just hitting the on
    override button on that room's timer/stat will bring it on, either to
    the next off time or for how ever many hours you select. Similarly
    hitting the off override button will turn heating for that room off, if
    you are not going to use it.

    If I were to do my house again, Id do it this way - a zone valve per
    room, timed and thermostat controlled .

    Once set up, things work pretty OK.

    --
    “when things get difficult you just have to lie”

    ― Jean Claud Jüncker

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From SteveW@21:1/5 to The Natural Philosopher on Mon Jan 20 17:59:16 2025
    On 20/01/2025 14:02, The Natural Philosopher wrote:
    On 20/01/2025 13:48, SteveW wrote:
    Most rooms tend to be used at the same times on the same day's each
    week (the timer/stats allow different programs to be allocated to each
    day if required, but we just use a weekday and a weekend program).

    If one is being used when it normally isn't, just hitting the on
    override button on that room's timer/stat will bring it on, either to
    the next off time or for how ever many hours you select. Similarly
    hitting the off override button will turn heating for that room off,
    if you are not going to use it.

    If I were to do my house again, Id do it this way - a zone valve per
    room, timed and thermostat controlled .

    Once set up, things work pretty OK.

    I did it because we had a baby (in 2003) and wanted to control the
    temperature in his room separately. At the time, Maplin were selling timer/thermostats for just £14 each and B&Q where having a clearance and selling off Honeywell motorised valves for just £18 each. At that price,
    I thought it well worth doing.