I wondered if this was something to do with the zone valve so as an experiment unplugged the relay. With the relay unplugged the pump
doesn't start, observing it when relay is plugged in it seems to be the
relay energising that starts the pump.
I will do a bit more digging and try and understand the wiring (maybe do
away with he zone valve as it doesn't actually work, I think the valve
is probably stuck open) and maybe return the wiring to classic Y plan.
Has anybody ever seen a motorised valve with an auxiliary relay, no
amount of googling finds one??
Gordon
On 26/01/2025 13:31, Gordy wrote:
I wondered if this was something to do with the zone valve so as an
experiment unplugged the relay. With the relay unplugged the pump
doesn't start, observing it when relay is plugged in it seems to be
the relay energising that starts the pump.
I will do a bit more digging and try and understand the wiring (maybe
do away with he zone valve as it doesn't actually work, I think the
valve is probably stuck open) and maybe return the wiring to classic Y
plan.
I would guess that the system is designed to run the pump, and boiler,
when the rest of the CH system is otherwise turned off, such as during
the night hours. The relay will bypass all of the other controls, so I
would expect there to be a room thermostat, somewhere upstairs, to limit
the temperature.
On 26/01/2025 13:31, Gordy wrote:
Has anybody ever seen a motorised valve with an auxiliary relay, no
amount of googling finds one??
Indeed. I had to install one in my central heating.
The problem is in my case was an auxiliary UFH pump. That didn't need to
come on when the boiler came on to heat upstairs.
So the UFH timer and thermostat controlled the UFH motorised valve which drove the UFH pump and a RELAY to switch the boiler on.
But if the upstairs or the DHW called for heat it *didn't* switch the
UFH pump on.
In practice it forms a sort of electromechanical OR gate. So upstairs OR downstairs can call for heat, but the one wont cause the other to operate
The problem is that the motorised valve only has one set of contacts,
the relay adds a second set. So the auxiliary pump is not energised by
the call for heat signal
Gordon
Hi all,
I was poking around in the airing cupboard weighing up how hard it's
going to be when I have to change the pump and noticed something I have
never come across before.
The system is a Y plan with an extra timer and zone valve (so that when
the heating is on Upstairs is either on or off depending on the extra
timer). I guess the idea is that you only want to heat downstairs in the
day.
Anyway I noticed that the motorised 3 port valve has some kind of
auxiliary relay plugged into the bottom of it (the same side as the
override lever)
I wondered if this was something to do with the zone valve so as an experiment unplugged the relay. With the relay unplugged the pump
doesn't start, observing it when relay is plugged in it seems to be the
relay energising that starts the pump.
I will do a bit more digging and try and understand the wiring (maybe do
away with he zone valve as it doesn't actually work, I think the valve
is probably stuck open) and maybe return the wiring to classic Y plan.
Has anybody ever seen a motorised valve with an auxiliary relay, no
amount of googling finds one??
Gordon
Hi,
I'm not sure it's that clever. There is no room thermostat anywhere on
the system and I was always under the impression that rather than it
being a true zone it simply either isolated or allowed the upstairs
heating whenever the main timer was selected to heating.
On 26/01/2025 13:51, The Natural Philosopher wrote:
On 26/01/2025 13:31, Gordy wrote:Did you find a valve with the relay, or add it yourself?
Has anybody ever seen a motorised valve with an auxiliary relay, no
amount of googling finds one??
Indeed. I had to install one in my central heating.
The problem is in my case was an auxiliary UFH pump. That didn't need
to come on when the boiler came on to heat upstairs.
So the UFH timer and thermostat controlled the UFH motorised valve
which drove the UFH pump and a RELAY to switch the boiler on.
But if the upstairs or the DHW called for heat it *didn't* switch the
UFH pump on.
In practice it forms a sort of electromechanical OR gate. So upstairs
OR downstairs can call for heat, but the one wont cause the other to
operate
The problem is that the motorised valve only has one set of contacts,
the relay adds a second set. So the auxiliary pump is not energised by
the call for heat signal
Gordon
My other issue is the plastic cover has broken off teh relay leaving
live contacts sticking out of the bottom of the valve
On 26/01/2025 13:41, Harry Bloomfield Esq wrote:
On 26/01/2025 13:31, Gordy wrote:
I wondered if this was something to do with the zone valve so as an
experiment unplugged the relay. With the relay unplugged the pump
doesn't start, observing it when relay is plugged in it seems to be
the relay energising that starts the pump.
I will do a bit more digging and try and understand the wiring (maybe
do away with he zone valve as it doesn't actually work, I think the
valve is probably stuck open) and maybe return the wiring to classic
Y plan.
I would guess that the system is designed to run the pump, and boiler,
when the rest of the CH system is otherwise turned off, such as during
the night hours. The relay will bypass all of the other controls, so I
would expect there to be a room thermostat, somewhere upstairs, to
limit the temperature.
Hi,
I'm not sure it's that clever. There is no room thermostat anywhere on
the system and I was always under the impression that rather than it
being a true zone it simply either isolated or allowed the upstairs
heating whenever the main timer was selected to heating.
Anyway I noticed that the motorised 3 port valve has some kind of
auxiliary relay plugged into the bottom of it (the same side as the
override lever)
I wondered if this was something to do with the zone valve so as an experiment unplugged the relay. With the relay unplugged the pump
doesn't start, observing it when relay is plugged in it seems to be the
relay energising that starts the pump.
Hi all,
I was poking around in the airing cupboard weighing up how hard it's
going to be when I have to change the pump and noticed something I have
never come across before.
The system is a Y plan with an extra timer and zone valve (so that when
the heating is on Upstairs is either on or off depending on the extra
timer). I guess the idea is that you only want to heat downstairs in the
day.
Anyway I noticed that the motorised 3 port valve has some kind of
auxiliary relay plugged into the bottom of it (the same side as the
override lever)
I wondered if this was something to do with the zone valve so as an experiment unplugged the relay. With the relay unplugged the pump
doesn't start, observing it when relay is plugged in it seems to be the
relay energising that starts the pump.
I will do a bit more digging and try and understand the wiring (maybe do
away with he zone valve as it doesn't actually work, I think the valve
is probably stuck open) and maybe return the wiring to classic Y plan.
Has anybody ever seen a motorised valve with an auxiliary relay, no
amount of googling finds one??
Gordon