• Neutral and earth

    From Scott@21:1/5 to All on Wed Mar 19 21:36:55 2025
    Why do we need separate neutral and earth wires when the neutral is
    earthed a the two are joined together at the point of entry anyway?
    Why not have two terminals - live and earth - and use the earth as the
    return path?

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From John Rumm@21:1/5 to Scott on Thu Mar 20 11:50:12 2025
    On 19/03/2025 21:36, Scott wrote:

    Why do we need separate neutral and earth wires

    Because they serve two completely different purposes. Neutral is a
    current carrying wire in normal use. Earth should not be current
    carrying, and is there as a path for current to pass under fault
    conditions. Neutral can be switched, earth should be a permanent
    connection. Neutral is classed as a "live" wire, earth is not etc.

    when the neutral is
    earthed a the two are joined together at the point of entry anyway?

    That depends on the earthing system in use; with TN-C-S (PME) then yes
    they are combined at the main cutout where the service enters the building.

    With TN-S, they are combined at a substation, not at the building.

    With TT, there is no earth provided at all by the suppler, you will need
    your own arrangement, and it is not necessarily connected to neutral at
    all.

    Why not have two terminals - live and earth - and use the earth as the
    return path?

    There is an earthing system TN-C (Where T = "Terre" aka Earth, N =
    Neutral, C = Combined), that does work as you describe - no separate
    earth, and neutral used as earth directly. However I don't think I have
    ever seen an installation like that in the UK, it is very uncommon.

    For more detail, see:

    https://wiki.diyfaq.org.uk/index.php/Earthing_Types#Earthing_Types


    --
    Cheers,

    John.

    /=================================================================\
    | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------|
    | John Rumm - john(at)internode(dot)co(dot)uk | \=================================================================/

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From jon@21:1/5 to John Rumm on Thu Mar 20 16:31:03 2025
    On Thu, 20 Mar 2025 11:50:12 +0000, John Rumm wrote:

    On 19/03/2025 21:36, Scott wrote:

    Why do we need separate neutral and earth wires

    Because they serve two completely different purposes. Neutral is a
    current carrying wire in normal use. Earth should not be current
    carrying, and is there as a path for current to pass under fault
    conditions. Neutral can be switched, earth should be a permanent
    connection. Neutral is classed as a "live" wire, earth is not etc.

    when the neutral is earthed a the two are joined together at the point
    of entry anyway?

    That depends on the earthing system in use; with TN-C-S (PME) then yes
    they are combined at the main cutout where the service enters the
    building.

    With TN-S, they are combined at a substation, not at the building.

    With TT, there is no earth provided at all by the suppler, you will need
    your own arrangement, and it is not necessarily connected to neutral at
    all.

    Why not have two terminals - live and earth - and use the earth as the
    return path?

    There is an earthing system TN-C (Where T = "Terre" aka Earth, N =
    Neutral, C = Combined), that does work as you describe - no separate
    earth, and neutral used as earth directly. However I don't think I have
    ever seen an installation like that in the UK, it is very uncommon.

    For more detail, see:

    https://wiki.diyfaq.org.uk/index.php/Earthing_Types#Earthing_Types

    You could switch off the isolator so all systems are dead and measure the resistance between the black and earth with a bonding meter.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From John Rumm@21:1/5 to jon on Thu Mar 20 17:30:43 2025
    On 20/03/2025 16:31, jon wrote:
    On Thu, 20 Mar 2025 11:50:12 +0000, John Rumm wrote:

    On 19/03/2025 21:36, Scott wrote:

    Why do we need separate neutral and earth wires

    Because they serve two completely different purposes. Neutral is a
    current carrying wire in normal use. Earth should not be current
    carrying, and is there as a path for current to pass under fault
    conditions. Neutral can be switched, earth should be a permanent
    connection. Neutral is classed as a "live" wire, earth is not etc.

    when the neutral is earthed a the two are joined together at the point
    of entry anyway?

    That depends on the earthing system in use; with TN-C-S (PME) then yes
    they are combined at the main cutout where the service enters the
    building.

    With TN-S, they are combined at a substation, not at the building.

    With TT, there is no earth provided at all by the suppler, you will need
    your own arrangement, and it is not necessarily connected to neutral at
    all.

    Why not have two terminals - live and earth - and use the earth as the
    return path?

    There is an earthing system TN-C (Where T = "Terre" aka Earth, N =
    Neutral, C = Combined), that does work as you describe - no separate
    earth, and neutral used as earth directly. However I don't think I have
    ever seen an installation like that in the UK, it is very uncommon.

    For more detail, see:

    https://wiki.diyfaq.org.uk/index.php/Earthing_Types#Earthing_Types

    You could switch off the isolator so all systems are dead and measure the resistance between the black and earth with a bonding meter.

    You would need to disconnect the main EQ bonding to get a reliable
    reading. Otherwise you could find yourself measuring the loop impedance
    through someone else's TN-C-S earth indirectly.

    --
    Cheers,

    John.

    /=================================================================\
    | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------|
    | John Rumm - john(at)internode(dot)co(dot)uk | \=================================================================/

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From jon@21:1/5 to John Rumm on Thu Mar 20 18:38:40 2025
    On Thu, 20 Mar 2025 17:30:43 +0000, John Rumm wrote:

    On 20/03/2025 16:31, jon wrote:
    On Thu, 20 Mar 2025 11:50:12 +0000, John Rumm wrote:

    On 19/03/2025 21:36, Scott wrote:

    Why do we need separate neutral and earth wires

    Because they serve two completely different purposes. Neutral is a
    current carrying wire in normal use. Earth should not be current
    carrying, and is there as a path for current to pass under fault
    conditions. Neutral can be switched, earth should be a permanent
    connection. Neutral is classed as a "live" wire, earth is not etc.

    when the neutral is earthed a the two are joined together at the
    point of entry anyway?

    That depends on the earthing system in use; with TN-C-S (PME) then yes
    they are combined at the main cutout where the service enters the
    building.

    With TN-S, they are combined at a substation, not at the building.

    With TT, there is no earth provided at all by the suppler, you will
    need your own arrangement, and it is not necessarily connected to
    neutral at all.

    Why not have two terminals - live and earth - and use the earth as
    the return path?

    There is an earthing system TN-C (Where T = "Terre" aka Earth, N =
    Neutral, C = Combined), that does work as you describe - no separate
    earth, and neutral used as earth directly. However I don't think I
    have ever seen an installation like that in the UK, it is very
    uncommon.

    For more detail, see:

    https://wiki.diyfaq.org.uk/index.php/Earthing_Types#Earthing_Types

    You could switch off the isolator so all systems are dead and measure
    the resistance between the black and earth with a bonding meter.

    You would need to disconnect the main EQ bonding to get a reliable
    reading. Otherwise you could find yourself measuring the loop impedance through someone else's TN-C-S earth indirectly.

    One would need to measure it first to determine if resistance is in the
    correct range.