• Earthrods. Indoors or out

    From tim+@21:1/5 to All on Wed May 28 14:11:55 2025
    We were looking into getting our home battery set up turned into
    an emergency power supply (which will require the fitting of
    earth rods).

    Our battery fitter has suggested fitting them into the soil under
    the house (which seems counterintuitive to be given how dry it
    must be). Is this okay (as long as the resistance is low enough)?


    Tim
    --

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From HVS@21:1/5 to John R Walliker on Wed May 28 15:10:42 2025
    On 28 May 2025, John R Walliker wrote

    On 28/05/2025 14:11, tim+ wrote:
    We were looking into getting our home battery set up turned into
    an emergency power supply (which will require the fitting of
    earth rods).

    Our battery fitter has suggested fitting them into the soil under
    the house (which seems counterintuitive to be given how dry it
    must be). Is this okay (as long as the resistance is low enough)?


    It is probably less dry than you imagine. You will avoid the risk
    of damage to an external earth rod and its neater as well.
    A good suggestion I think.

    FWIW, I was under the impression that the soil under the house was an
    extremely common position for an earth rod; I'd probably assume that's
    still the case.

    --
    Cheers, Harvey

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From The Natural Philosopher@21:1/5 to HVS on Wed May 28 15:19:16 2025
    On 28/05/2025 15:10, HVS wrote:
    On 28 May 2025, John R Walliker wrote

    On 28/05/2025 14:11, tim+ wrote:
    We were looking into getting our home battery set up turned into
    an emergency power supply (which will require the fitting of
    earth rods).

    Our battery fitter has suggested fitting them into the soil under
    the house (which seems counterintuitive to be given how dry it
    must be). Is this okay (as long as the resistance is low enough)?


    It is probably less dry than you imagine. You will avoid the risk
    of damage to an external earth rod and its neater as well.
    A good suggestion I think.

    FWIW, I was under the impression that the soil under the house was an extremely common position for an earth rod; I'd probably assume that's
    still the case.

    Mine is simply pounded into the clay 2 inches from the wall where the electricity supply comes in

    --
    "I guess a rattlesnake ain't risponsible fer bein' a rattlesnake, but ah
    puts mah heel on um jess the same if'n I catches him around mah chillun".

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Scott@21:1/5 to timdownieuk@yahoo.co.uk on Wed May 28 15:41:46 2025
    On Wed, 28 May 2025 14:11:55 +0100 (GMT+01:00), tim+
    <timdownieuk@yahoo.co.uk> wrote:

    We were looking into getting our home battery set up turned into
    an emergency power supply (which will require the fitting of
    earth rods).

    Our battery fitter has suggested fitting them into the soil under
    the house (which seems counterintuitive to be given how dry it
    must be). Is this okay (as long as the resistance is low enough)?

    Excuse my igorance but why are earth rods needed? Could the ordinary
    electrical earth not be used? Is it because the emergency could
    involve damage to the neutral/earth outside?

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From tim+@21:1/5 to John R Walliker on Wed May 28 16:40:49 2025
    John R Walliker <jrwalliker@gmail.com> Wrote in message:r
    On 28/05/2025 14:11, tim+ wrote:> We were looking into getting our home battery set up turned into> an emergency power supply (which will require the fitting of> earth rods).> > Our battery fitter has suggested fitting them into the soil under>
    the house (which seems counterintuitive to be given how dry it> must be). Is this okay (as long as the resistance is low enough)?>It is probably less dry than you imagine. You will avoid the riskof damage to an external earth rod and its neater as
    well.A good suggestion I think.John

    Thanks, that's reassuring.

    A follow question regarding the practical aspects of installing.
    Our understairs cupboard has limited headroom. A nearby cupboard
    has plenty of headroom but lots of pipes in the subfloor space.
    All visible but not much room to work if width is needed. Which
    would be better?

    Tim

    --

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From tim+@21:1/5 to Scott on Wed May 28 16:37:06 2025
    Scott <newsgroups@gefion.myzen.co.uk> Wrote in message:r
    On Wed, 28 May 2025 14:11:55 +0100 (GMT+01:00), tim+<timdownieuk@yahoo.co.uk> wrote:>We were looking into getting our home battery set up turned into> an emergency power supply (which will require the fitting of> earth rods). >>Our battery fitter has
    suggested fitting them into the soil under> the house (which seems counterintuitive to be given how dry it> must be). Is this okay (as long as the resistance is low enough)?> Excuse my igorance but why are earth rods needed? Could the ordinaryelectrical
    earth not be used? Is it because the emergency couldinvolve damage to the neutral/earth outside?

    Yes, exactly this.

    Tim
    --

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From David Wade@21:1/5 to All on Wed May 28 16:48:48 2025
    On 28/05/2025 14:11, tim+ wrote:
    We were looking into getting our home battery set up turned into
    an emergency power supply (which will require the fitting of
    earth rods).

    Our battery fitter has suggested fitting them into the soil under
    the house (which seems counterintuitive to be given how dry it
    must be). Is this okay (as long as the resistance is low enough)?


    I think the usual reason for an outside earth is that most modern houses
    are built with a solid ground floor, or with a concrete "raft" as he foundations. There should be a barrier membrane, so you can't drill
    through it without affecting the membrane.

    If you have plain soil underneath It would seem the logical place to put
    it. The moisture content under the house is likely to be more stable, so
    once a value has been measured, whereas one outside would experience and
    so perhaps get too high in a drought



    Tim

    Dave

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Tricky Dicky@21:1/5 to Scott on Wed May 28 15:58:07 2025
    Scott <newsgroups@gefion.myzen.co.uk> wrote:

    Excuse my igorance but why are earth rods needed? Could the ordinary electrical earth not be used? Is it because the emergency could
    involve damage to the neutral/earth outside?


    John Ward explains what the possible problems are and the options

    https://youtu.be/gZVx7GbAwlg?si=mIFPnNb7QEPtdvhR

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From alan_m@21:1/5 to All on Wed May 28 18:57:45 2025
    On 28/05/2025 16:40, tim+ wrote:
    John R Walliker <jrwalliker@gmail.com> Wrote in message:r
    On 28/05/2025 14:11, tim+ wrote:> We were looking into getting our home battery set up turned into> an emergency power supply (which will require the fitting of> earth rods).> > Our battery fitter has suggested fitting them into the soil under>
    the house (which seems counterintuitive to be given how dry it> must be). Is this okay (as long as the resistance is low enough)?>It is probably less dry than you imagine. You will avoid the riskof damage to an external earth rod and its neater as
    well.A good suggestion I think.John

    Thanks, that's reassuring.

    A follow question regarding the practical aspects of installing.
    Our understairs cupboard has limited headroom. A nearby cupboard
    has plenty of headroom but lots of pipes in the subfloor space.
    All visible but not much room to work if width is needed. Which
    would be better?

    Tim


    As a matter of interest where are the batteries to be installed, or
    are installed?

    I was under the impression they could no longer be installed in a loft
    space or under stairs for fire access and safety concerns. If installed
    indoors fire safety and methods of exit in the event of a fire must also
    be considered. If fitted on an outside wall there is a minimum distance
    to any window or door.

    Would modification to an existing battery fitting also have to consider
    the above.

    --
    mailto : news {at} admac {dot} myzen {dot} co {dot} uk

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Tim+@21:1/5 to junk@admac.myzen.co.uk on Wed May 28 18:17:22 2025
    alan_m <junk@admac.myzen.co.uk> wrote:
    On 28/05/2025 16:40, tim+ wrote:
    John R Walliker <jrwalliker@gmail.com> Wrote in message:r
    On 28/05/2025 14:11, tim+ wrote:> We were looking into getting our home
    battery set up turned into> an emergency power supply (which will
    require the fitting of> earth rods).> > Our battery fitter has
    suggested fitting them into the soil under> the house (which seems
    counterintuitive to be given how dry it> must be). Is this okay (as
    long as the resistance is low enough)?>It is probably less dry than you
    imagine. You will avoid the riskof damage to an external earth rod and
    its neater as well.A good suggestion I think.John

    Thanks, that's reassuring.

    A follow question regarding the practical aspects of installing.
    Our understairs cupboard has limited headroom. A nearby cupboard
    has plenty of headroom but lots of pipes in the subfloor space.
    All visible but not much room to work if width is needed. Which
    would be better?

    Tim


    As a matter of interest where are the batteries to be installed, or
    are installed?

    Loft


    I was under the impression they could no longer be installed in a loft
    space or under stairs for fire access and safety concerns.

    No, it’s just an advisory. As they’re lithium iron phosphate batteries I have no concerns.

    https://www.pretapower.com/lifepo4-battery-fire-what-you-need-to-know/#:~:text=They%20are%20known%20explicitly%20for,have%20extremely%20minimal%20fire%20risk.


    Tim

    --
    Please don't feed the trolls

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Scott@21:1/5 to tricky.dicky@sky.com on Wed May 28 20:44:45 2025
    On Wed, 28 May 2025 15:58:07 -0000 (UTC), Tricky Dicky
    <tricky.dicky@sky.com> wrote:

    Scott <newsgroups@gefion.myzen.co.uk> wrote:

    Excuse my igorance but why are earth rods needed? Could the ordinary
    electrical earth not be used? Is it because the emergency could
    involve damage to the neutral/earth outside?

    John Ward explains what the possible problems are and the options >https://youtu.be/gZVx7GbAwlg?si=mIFPnNb7QEPtdvhR

    I like John Ward. He is a clear communicator. He would make a good
    expert witness,