t. Switching on the immersion and burglar
alarm MCBs leaves the RCD unaffected but switching the other three trips
it. Sometimes switching on the ring main MCB has no effect but as soon as
a load is applied the RCD trips.
On 26/06/2025 00:07, Tricky Dicky wrote:
t. Switching on the immersion and burglar
alarm MCBs leaves the RCD unaffected but switching the other three trips
it. Sometimes switching on the ring main MCB has no effect but as
soon as
a load is applied the RCD trips.
Theres your problem.
It could be a neutral to earth fault. Get it tested properly with a good ohmmeter, preferably one that is used for electrical installations,
rather than a cheap £10 one from Wilko.
My daughter has an RCD that keeps tripping and I cannot find the fault. Out of the blue this evening it just tripped without any particular reason and she could not identify what she did to cause it to trip.
The RCD is one of two in a split CU with MCBs for the immersion, downstairs ring main, garage feed. Upstairs lights and burglar alarm. I have tried the usual process to at least identify which circuit is at fault by switching
off all the MCBs, resetting the RCD and switching each individual MCB on to see which is the faulty circuit. Switching on the immersion and burglar
alarm MCBs leaves the RCD unaffected but switching the other three trips
it. Sometimes switching on the ring main MCB has no effect but as soon as
a load is applied the RCD trips. Does this suggest that the RCD is faulty
or is there another possible fault? Pressing the test button causes it to trip as normal.
Richard
On 26/06/2025 00:07, Tricky Dicky wrote:
My daughter has an RCD that keeps tripping and I cannot find the fault. Out >> of the blue this evening it just tripped without any particular reason and >> she could not identify what she did to cause it to trip.
The RCD is one of two in a split CU with MCBs for the immersion, downstairs >> ring main, garage feed. Upstairs lights and burglar alarm. I have tried the >> usual process to at least identify which circuit is at fault by switching
off all the MCBs, resetting the RCD and switching each individual MCB on to >> see which is the faulty circuit. Switching on the immersion and burglar
alarm MCBs leaves the RCD unaffected but switching the other three trips
it. Sometimes switching on the ring main MCB has no effect but as soon as >> a load is applied the RCD trips. Does this suggest that the RCD is faulty
or is there another possible fault? Pressing the test button causes it to
trip as normal.
Richard
It sounds very much like you have an earth neutral short.
I had one for years.
The only way to ID is to first of all ID which ring - switch off the
whole CU and disconnect each neutral in turn and measure neutral to
ground resistance. (You should remove all un-pluggable appliances first) .
Then when you have the circuit Id'ed you need to measure neutral to
ground resistance..as you get closer to the short, resistance will decrease.
After that it is a matter of inspection.
If the rings and spurs check out, it may well be an appliance. Electric motors have been known to short a turn to ground.
Note that this is a tedious step by step process of elimination and an electrician is going to charge.
The Natural Philosopher <tnp@invalid.invalid> wrote:
On 26/06/2025 00:07, Tricky Dicky wrote:
My daughter has an RCD that keeps tripping and I cannot find the fault. Out >>> of the blue this evening it just tripped without any particular reason and >>> she could not identify what she did to cause it to trip.
The RCD is one of two in a split CU with MCBs for the immersion, downstairs >>> ring main, garage feed. Upstairs lights and burglar alarm. I have tried the >>> usual process to at least identify which circuit is at fault by switching >>> off all the MCBs, resetting the RCD and switching each individual MCB on to >>> see which is the faulty circuit. Switching on the immersion and burglar
alarm MCBs leaves the RCD unaffected but switching the other three trips >>> it. Sometimes switching on the ring main MCB has no effect but as soon as >>> a load is applied the RCD trips. Does this suggest that the RCD is faulty >>> or is there another possible fault? Pressing the test button causes it to >>> trip as normal.
Richard
It sounds very much like you have an earth neutral short.
I had one for years.
The only way to ID is to first of all ID which ring - switch off the
whole CU and disconnect each neutral in turn and measure neutral to
ground resistance. (You should remove all un-pluggable appliances first) . >>
Then when you have the circuit Id'ed you need to measure neutral to
ground resistance..as you get closer to the short, resistance will decrease. >>
After that it is a matter of inspection.
If the rings and spurs check out, it may well be an appliance. Electric
motors have been known to short a turn to ground.
Note that this is a tedious step by step process of elimination and an
electrician is going to charge.
Thanks for the explanation. He has managed to get an electrician in who should be working on the problem as I type.
Just out of interest when isolating the neutrals do you have to do all of them as it is a split CU and the the other half of the CU is working as it should?
The Natural Philosopher <tnp@invalid.invalid> wrote:
On 26/06/2025 00:07, Tricky Dicky wrote:
My daughter has an RCD that keeps tripping and I cannot find the fault. Out >>> of the blue this evening it just tripped without any particular reason and >>> she could not identify what she did to cause it to trip.
The RCD is one of two in a split CU with MCBs for the immersion, downstairs >>> ring main, garage feed. Upstairs lights and burglar alarm. I have tried the >>> usual process to at least identify which circuit is at fault by switching >>> off all the MCBs, resetting the RCD and switching each individual MCB on to >>> see which is the faulty circuit. Switching on the immersion and burglar
alarm MCBs leaves the RCD unaffected but switching the other three trips >>> it. Sometimes switching on the ring main MCB has no effect but as soon as >>> a load is applied the RCD trips. Does this suggest that the RCD is faulty >>> or is there another possible fault? Pressing the test button causes it to >>> trip as normal.
Richard
It sounds very much like you have an earth neutral short.
I had one for years.
The only way to ID is to first of all ID which ring - switch off the
whole CU and disconnect each neutral in turn and measure neutral to
ground resistance. (You should remove all un-pluggable appliances first) . >>
Then when you have the circuit Id'ed you need to measure neutral to
ground resistance..as you get closer to the short, resistance will decrease. >>
After that it is a matter of inspection.
If the rings and spurs check out, it may well be an appliance. Electric
motors have been known to short a turn to ground.
Note that this is a tedious step by step process of elimination and an
electrician is going to charge.
Thanks for the explanation. He has managed to get an electrician in who should be working on the problem as I type.
Just out of interest when isolating the neutrals do you have to do all of them as it is a split CU and the the other half of the CU is working as it should?
In article <103iq6n$3ag63$1@dont-email.me>, Alan Lee
<alan@darkroom.plus.com> scribeth thus
On 26/06/2025 00:07, Tricky Dicky wrote:
t. Switching on the immersion and burglar
alarm MCBs leaves the RCD unaffected but switching the other three trips >>> it. Sometimes switching on the ring main MCB has no effect but as soon as >>> a load is applied the RCD trips.
Theres your problem.
It could be a neutral to earth fault. Get it tested properly with a good
ohmmeter, preferably one that is used for electrical installations,
rather than a cheap £10 one from Wilko.
Second that!, it needs some current to flow _before_ that will show up
as a fault as such..
Second to the good multimeter!, if you can find one a second hand Fluke
is a very good choice may not have all the bells and whistles but
manage fine with mine in an Electronics workshop!..
On 26/06/2025 00:07, Tricky Dicky wrote:
t. Switching on the immersion and burglar
alarm MCBs leaves the RCD unaffected but switching the other three trips
it. Sometimes switching on the ring main MCB has no effect but as soon as >> a load is applied the RCD trips.
Theres your problem.
It could be a neutral to earth fault. Get it tested properly with a good >ohmmeter, preferably one that is used for electrical installations,
rather than a cheap 10 one from Wilko.
My downstairs RCD tripped one evening a couple of weeks ago, for no
obvious reason. Narrowed the issue down to the outside lighting
circuits so turned if off. Couldn't see anything obviously wrong with
the lighting, and some of it would require ladder work to access, so I changed the screw terminals in various junction boxes for Wagos, not
seeing anything wrong as I did so, and turned the power back on. Been
OK since but it must be a coincidence.
My daughter has an RCD that keeps tripping and I cannot find the fault. Out >of the blue this evening it just tripped without any particular reason and >she could not identify what she did to cause it to trip.
On Wed, 25 Jun 2025 23:07:52 -0000 (UTC), Tricky Dicky ><tricky.dicky@sky.com> wrote:
My daughter has an RCD that keeps tripping and I cannot find the fault. Out >>of the blue this evening it just tripped without any particular reason and >>she could not identify what she did to cause it to trip.
My downstairs RCD tripped one evening a couple of weeks ago, for no
obvious reason. Narrowed the issue down to the outside lighting
circuits so turned if off. Couldn't see anything obviously wrong with
the lighting, and some of it would require ladder work to access, so I >changed the screw terminals in various junction boxes for Wagos, not
seeing anything wrong as I did so, and turned the power back on. Been
OK since but it must be a coincidence.
Peter Johnson <peter@parksidewood.nospam> wrote:
My downstairs RCD tripped one evening a couple of weeks ago, for no
obvious reason. Narrowed the issue down to the outside lighting
circuits so turned if off. Couldn't see anything obviously wrong with
the lighting, and some of it would require ladder work to access, so I
changed the screw terminals in various junction boxes for Wagos, not
seeing anything wrong as I did so, and turned the power back on. Been
OK since but it must be a coincidence.
Water getting in? It could trip when it rains and then the fault clears
when it's dried out? Or something similar with a slug or other conductive >beastie.