• RCD tripping

    From Tricky Dicky@21:1/5 to All on Wed Jun 25 23:07:52 2025
    My daughter has an RCD that keeps tripping and I cannot find the fault. Out
    of the blue this evening it just tripped without any particular reason and
    she could not identify what she did to cause it to trip.

    The RCD is one of two in a split CU with MCBs for the immersion, downstairs ring main, garage feed. Upstairs lights and burglar alarm. I have tried the usual process to at least identify which circuit is at fault by switching
    off all the MCBs, resetting the RCD and switching each individual MCB on to
    see which is the faulty circuit. Switching on the immersion and burglar
    alarm MCBs leaves the RCD unaffected but switching the other three trips
    it. Sometimes switching on the ring main MCB has no effect but as soon as
    a load is applied the RCD trips. Does this suggest that the RCD is faulty
    or is there another possible fault? Pressing the test button causes it to
    trip as normal.

    Richard

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Alan Lee@21:1/5 to Tricky Dicky on Thu Jun 26 07:43:35 2025
    On 26/06/2025 00:07, Tricky Dicky wrote:
    t. Switching on the immersion and burglar
    alarm MCBs leaves the RCD unaffected but switching the other three trips
    it. Sometimes switching on the ring main MCB has no effect but as soon as
    a load is applied the RCD trips.


    Theres your problem.
    It could be a neutral to earth fault. Get it tested properly with a good ohmmeter, preferably one that is used for electrical installations,
    rather than a cheap £10 one from Wilko.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From The Natural Philosopher@21:1/5 to Alan Lee on Thu Jun 26 11:14:21 2025
    On 26/06/2025 07:43, Alan Lee wrote:
    On 26/06/2025 00:07, Tricky Dicky wrote:
    t. Switching on the immersion and burglar
    alarm MCBs leaves the RCD unaffected but switching the other three trips
    it. Sometimes switching on the  ring main MCB has no effect but as
    soon as
    a load is applied the RCD trips.


    Theres your problem.
    It could be a neutral to earth fault. Get it tested properly with a good ohmmeter, preferably one that is used for electrical installations,
    rather than a cheap £10 one from Wilko.

    +1

    --
    The urge to save humanity is almost always a false front for the urge to
    rule.
    – H. L. Mencken, American journalist, 1880-1956

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From The Natural Philosopher@21:1/5 to Tricky Dicky on Thu Jun 26 11:13:53 2025
    On 26/06/2025 00:07, Tricky Dicky wrote:

    My daughter has an RCD that keeps tripping and I cannot find the fault. Out of the blue this evening it just tripped without any particular reason and she could not identify what she did to cause it to trip.

    The RCD is one of two in a split CU with MCBs for the immersion, downstairs ring main, garage feed. Upstairs lights and burglar alarm. I have tried the usual process to at least identify which circuit is at fault by switching
    off all the MCBs, resetting the RCD and switching each individual MCB on to see which is the faulty circuit. Switching on the immersion and burglar
    alarm MCBs leaves the RCD unaffected but switching the other three trips
    it. Sometimes switching on the ring main MCB has no effect but as soon as
    a load is applied the RCD trips. Does this suggest that the RCD is faulty
    or is there another possible fault? Pressing the test button causes it to trip as normal.

    Richard

    It sounds very much like you have an earth neutral short.

    I had one for years.

    The only way to ID is to first of all ID which ring - switch off the
    whole CU and disconnect each neutral in turn and measure neutral to
    ground resistance. (You should remove all un-pluggable appliances first) .

    Then when you have the circuit Id'ed you need to measure neutral to
    ground resistance..as you get closer to the short, resistance will decrease.

    After that it is a matter of inspection.

    If the rings and spurs check out, it may well be an appliance. Electric
    motors have been known to short a turn to ground.

    Note that this is a tedious step by step process of elimination and an electrician is going to charge.


    --
    All political activity makes complete sense once the proposition that
    all government is basically a self-legalising protection racket, is
    fully understood.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Tricky Dicky@21:1/5 to The Natural Philosopher on Thu Jun 26 10:29:40 2025
    The Natural Philosopher <tnp@invalid.invalid> wrote:
    On 26/06/2025 00:07, Tricky Dicky wrote:

    My daughter has an RCD that keeps tripping and I cannot find the fault. Out >> of the blue this evening it just tripped without any particular reason and >> she could not identify what she did to cause it to trip.

    The RCD is one of two in a split CU with MCBs for the immersion, downstairs >> ring main, garage feed. Upstairs lights and burglar alarm. I have tried the >> usual process to at least identify which circuit is at fault by switching
    off all the MCBs, resetting the RCD and switching each individual MCB on to >> see which is the faulty circuit. Switching on the immersion and burglar
    alarm MCBs leaves the RCD unaffected but switching the other three trips
    it. Sometimes switching on the ring main MCB has no effect but as soon as >> a load is applied the RCD trips. Does this suggest that the RCD is faulty
    or is there another possible fault? Pressing the test button causes it to
    trip as normal.

    Richard

    It sounds very much like you have an earth neutral short.

    I had one for years.

    The only way to ID is to first of all ID which ring - switch off the
    whole CU and disconnect each neutral in turn and measure neutral to
    ground resistance. (You should remove all un-pluggable appliances first) .

    Then when you have the circuit Id'ed you need to measure neutral to
    ground resistance..as you get closer to the short, resistance will decrease.

    After that it is a matter of inspection.

    If the rings and spurs check out, it may well be an appliance. Electric motors have been known to short a turn to ground.

    Note that this is a tedious step by step process of elimination and an electrician is going to charge.



    Thanks for the explanation. He has managed to get an electrician in who
    should be working on the problem as I type.

    Just out of interest when isolating the neutrals do you have to do all of
    them as it is a split CU and the the other half of the CU is working as it should?

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Tricky Dicky@21:1/5 to Dicky on Thu Jun 26 11:57:15 2025
    Tricky Dicky <tricky.dicky@sky.com> wrote:
    The Natural Philosopher <tnp@invalid.invalid> wrote:
    On 26/06/2025 00:07, Tricky Dicky wrote:

    My daughter has an RCD that keeps tripping and I cannot find the fault. Out >>> of the blue this evening it just tripped without any particular reason and >>> she could not identify what she did to cause it to trip.

    The RCD is one of two in a split CU with MCBs for the immersion, downstairs >>> ring main, garage feed. Upstairs lights and burglar alarm. I have tried the >>> usual process to at least identify which circuit is at fault by switching >>> off all the MCBs, resetting the RCD and switching each individual MCB on to >>> see which is the faulty circuit. Switching on the immersion and burglar
    alarm MCBs leaves the RCD unaffected but switching the other three trips >>> it. Sometimes switching on the ring main MCB has no effect but as soon as >>> a load is applied the RCD trips. Does this suggest that the RCD is faulty >>> or is there another possible fault? Pressing the test button causes it to >>> trip as normal.

    Richard

    It sounds very much like you have an earth neutral short.

    I had one for years.

    The only way to ID is to first of all ID which ring - switch off the
    whole CU and disconnect each neutral in turn and measure neutral to
    ground resistance. (You should remove all un-pluggable appliances first) . >>
    Then when you have the circuit Id'ed you need to measure neutral to
    ground resistance..as you get closer to the short, resistance will decrease. >>
    After that it is a matter of inspection.

    If the rings and spurs check out, it may well be an appliance. Electric
    motors have been known to short a turn to ground.

    Note that this is a tedious step by step process of elimination and an
    electrician is going to charge.



    Thanks for the explanation. He has managed to get an electrician in who should be working on the problem as I type.

    Just out of interest when isolating the neutrals do you have to do all of them as it is a split CU and the the other half of the CU is working as it should?



    An update. The sparky has been and isolated the issue to the upstairs
    lighting circuit but owing to the mixture of wiring systems ie loop-in at
    the rosette and loop-in at the switch has not been able to solve the
    problem yet. Owing to having to go to another job he has isolated the
    upstairs lights which has allowed all the other circuits on that RCD to
    work and will come back later to do some more testing. My SiL did say he
    spent quite a time at one switch on the middle floor.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From The Natural Philosopher@21:1/5 to Tricky Dicky on Thu Jun 26 13:42:49 2025
    On 26/06/2025 11:29, Tricky Dicky wrote:
    The Natural Philosopher <tnp@invalid.invalid> wrote:
    On 26/06/2025 00:07, Tricky Dicky wrote:

    My daughter has an RCD that keeps tripping and I cannot find the fault. Out >>> of the blue this evening it just tripped without any particular reason and >>> she could not identify what she did to cause it to trip.

    The RCD is one of two in a split CU with MCBs for the immersion, downstairs >>> ring main, garage feed. Upstairs lights and burglar alarm. I have tried the >>> usual process to at least identify which circuit is at fault by switching >>> off all the MCBs, resetting the RCD and switching each individual MCB on to >>> see which is the faulty circuit. Switching on the immersion and burglar
    alarm MCBs leaves the RCD unaffected but switching the other three trips >>> it. Sometimes switching on the ring main MCB has no effect but as soon as >>> a load is applied the RCD trips. Does this suggest that the RCD is faulty >>> or is there another possible fault? Pressing the test button causes it to >>> trip as normal.

    Richard

    It sounds very much like you have an earth neutral short.

    I had one for years.

    The only way to ID is to first of all ID which ring - switch off the
    whole CU and disconnect each neutral in turn and measure neutral to
    ground resistance. (You should remove all un-pluggable appliances first) . >>
    Then when you have the circuit Id'ed you need to measure neutral to
    ground resistance..as you get closer to the short, resistance will decrease. >>
    After that it is a matter of inspection.

    If the rings and spurs check out, it may well be an appliance. Electric
    motors have been known to short a turn to ground.

    Note that this is a tedious step by step process of elimination and an
    electrician is going to charge.



    Thanks for the explanation. He has managed to get an electrician in who should be working on the problem as I type.

    Just out of interest when isolating the neutrals do you have to do all of them as it is a split CU and the the other half of the CU is working as it should?

    No. Just the ones associated with the trip

    --
    "An intellectual is a person knowledgeable in one field who speaks out
    only in others...”

    Tom Wolfe

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From The Natural Philosopher@21:1/5 to tony sayer on Thu Jun 26 13:45:08 2025
    On 26/06/2025 13:20, tony sayer wrote:
    In article <103iq6n$3ag63$1@dont-email.me>, Alan Lee
    <alan@darkroom.plus.com> scribeth thus
    On 26/06/2025 00:07, Tricky Dicky wrote:
    t. Switching on the immersion and burglar
    alarm MCBs leaves the RCD unaffected but switching the other three trips >>> it. Sometimes switching on the ring main MCB has no effect but as soon as >>> a load is applied the RCD trips.


    Theres your problem.
    It could be a neutral to earth fault. Get it tested properly with a good
    ohmmeter, preferably one that is used for electrical installations,
    rather than a cheap £10 one from Wilko.

    Second that!, it needs some current to flow _before_ that will show up
    as a fault as such..


    Second to the good multimeter!, if you can find one a second hand Fluke
    is a very good choice may not have all the bells and whistles but
    manage fine with mine in an Electronics workshop!..

    I got an antique AVOMeter Mk II for £45 at a antique shop.
    So nice to have a reliable meter with a moving needle again


    --
    “Progress is precisely that which rules and regulations did not foresee,”

    – Ludwig von Mises

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From tony sayer@21:1/5 to All on Thu Jun 26 13:20:29 2025
    In article <103iq6n$3ag63$1@dont-email.me>, Alan Lee
    <alan@darkroom.plus.com> scribeth thus
    On 26/06/2025 00:07, Tricky Dicky wrote:
    t. Switching on the immersion and burglar
    alarm MCBs leaves the RCD unaffected but switching the other three trips
    it. Sometimes switching on the ring main MCB has no effect but as soon as >> a load is applied the RCD trips.


    Theres your problem.
    It could be a neutral to earth fault. Get it tested properly with a good >ohmmeter, preferably one that is used for electrical installations,
    rather than a cheap 10 one from Wilko.

    Second that!, it needs some current to flow _before_ that will show up
    as a fault as such..


    Second to the good multimeter!, if you can find one a second hand Fluke
    is a very good choice may not have all the bells and whistles but
    manage fine with mine in an Electronics workshop!..
    --
    Tony Sayer


    Man is least himself when he talks in his own person.

    Give him a keyboard, and he will reveal himself.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Theo@21:1/5 to Peter Johnson on Thu Jun 26 17:26:58 2025
    Peter Johnson <peter@parksidewood.nospam> wrote:
    My downstairs RCD tripped one evening a couple of weeks ago, for no
    obvious reason. Narrowed the issue down to the outside lighting
    circuits so turned if off. Couldn't see anything obviously wrong with
    the lighting, and some of it would require ladder work to access, so I changed the screw terminals in various junction boxes for Wagos, not
    seeing anything wrong as I did so, and turned the power back on. Been
    OK since but it must be a coincidence.

    Water getting in? It could trip when it rains and then the fault clears
    when it's dried out? Or something similar with a slug or other conductive beastie.

    Theo

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Peter Johnson@21:1/5 to tricky.dicky@sky.com on Thu Jun 26 17:22:42 2025
    On Wed, 25 Jun 2025 23:07:52 -0000 (UTC), Tricky Dicky
    <tricky.dicky@sky.com> wrote:


    My daughter has an RCD that keeps tripping and I cannot find the fault. Out >of the blue this evening it just tripped without any particular reason and >she could not identify what she did to cause it to trip.


    My downstairs RCD tripped one evening a couple of weeks ago, for no
    obvious reason. Narrowed the issue down to the outside lighting
    circuits so turned if off. Couldn't see anything obviously wrong with
    the lighting, and some of it would require ladder work to access, so I
    changed the screw terminals in various junction boxes for Wagos, not
    seeing anything wrong as I did so, and turned the power back on. Been
    OK since but it must be a coincidence.

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From AnthonyL@21:1/5 to peter@parksidewood.nospam on Fri Jun 27 11:44:01 2025
    On Thu, 26 Jun 2025 17:22:42 +0100, Peter Johnson
    <peter@parksidewood.nospam> wrote:

    On Wed, 25 Jun 2025 23:07:52 -0000 (UTC), Tricky Dicky ><tricky.dicky@sky.com> wrote:


    My daughter has an RCD that keeps tripping and I cannot find the fault. Out >>of the blue this evening it just tripped without any particular reason and >>she could not identify what she did to cause it to trip.


    My downstairs RCD tripped one evening a couple of weeks ago, for no
    obvious reason. Narrowed the issue down to the outside lighting
    circuits so turned if off. Couldn't see anything obviously wrong with
    the lighting, and some of it would require ladder work to access, so I >changed the screw terminals in various junction boxes for Wagos, not
    seeing anything wrong as I did so, and turned the power back on. Been
    OK since but it must be a coincidence.

    For quite a few years we had an RCD trip, seemingly at random until I
    realised it happened when my wife was roasting meat. This in itself
    didn't make a lot of sense since there were no problems with baking.
    However it then dawned on my that above but not quite to the side of
    the hobs was the unswitched oven fuse which got partially covered when
    the hob lid was raised. eg:

    https://www.wellingtonshomeelectrical.co.uk/images/thumbs/0007339_leisure-cc100f521c-chefmaster-100cm-dual-fuel-range-cooker-with-glass-top-lid-in-cream_600.jpeg

    The box was slightly adrift of the wall and taping up the sides has sufficiently sealed it to the wall such that any condensation trapped
    by the raised lid would not seep into the fuse. Pulling the oven away
    from the wall a fraction also helped any steam arising to escape.
    --
    AnthonyL

    Why ever wait to finish a job before starting the next?

    --- SoupGate-Win32 v1.05
    * Origin: fsxNet Usenet Gateway (21:1/5)
  • From Peter Johnson@21:1/5 to theom+news@chiark.greenend.org.uk on Fri Jun 27 20:15:16 2025
    On 26 Jun 2025 17:26:58 +0100 (BST), Theo
    <theom+news@chiark.greenend.org.uk> wrote:

    Peter Johnson <peter@parksidewood.nospam> wrote:
    My downstairs RCD tripped one evening a couple of weeks ago, for no
    obvious reason. Narrowed the issue down to the outside lighting
    circuits so turned if off. Couldn't see anything obviously wrong with
    the lighting, and some of it would require ladder work to access, so I
    changed the screw terminals in various junction boxes for Wagos, not
    seeing anything wrong as I did so, and turned the power back on. Been
    OK since but it must be a coincidence.

    Water getting in? It could trip when it rains and then the fault clears
    when it's dried out? Or something similar with a slug or other conductive >beastie.


    Don't think so. Not had much rain lately and everything external is
    well sealed.

    For a few weeks the living room intruder sensor had been triggering
    during the night, the alarm sounding long enough to wake me but not
    long enough to bother the neighbours. Once that happened at about
    8.00am and I went downstairs to find that the RCD had tripped and the
    intruder panel battery was flat. No way of telling what the sequence
    of events was but it was a bit weird. The alarm installer changed the
    battery and so far the sensor hasn't been triggered and the RCD hasn't
    tripped so one way or another everything seems to be OK.